Flex Chassis Fan Redundancy

2021-05-26, 3:05 AM

Hi,

What is the redundancy level on fans in Flex Chassis? Is it N+N / N+1 redundancy?

 

Below link refer to 4 Zones on the Flex Chassis

https://flexsystem.lenovofiles.com/help/index.jsp?topic=%2Fcom.lenovo.acc.8721.doc%2Ffans.html

 

Zone 1 with 80 mm fans slot 1, 2, 3, 4 provide cooling for the odd-numbered node bays 1, 3, 5, 7, 9, 11, and 13.

 

Zone 2 with 80 mm fans slot 6, 7, 8, 9 provide cooling for the odd-numbered node bays 2, 4, 6, 8, 10, 12, and 14.

 

Zone 3 with 40 mm fan slot 5 provide cooling for IOMs 2, 4 and CMMs.

 

Zone 4 with 40 mm fan slot 10 provide cooling for IOMs 1 and 3.

 

- What happens if Zone 1 fans (ie 1, 2, 3, 4) fails? Will the blades continue to run from the Zone 2 fans?

- What happens if Zone 3 fan (ie 5) fails? Will IOMs 2, 4 goes down?

 

 

 

Reply
Answer
Options

82 Posts

04-23-2015

Japan

167 Signins

989 Page Views

  • Posts: 82
  • Registered: ‎04-23-2015
  • Location: Japan
  • Views: 989

Re:Flex Chassis Fan Redundancy

2021-05-27, 0:44 AM

Hi Errrec,

 

Each zones are separated and cannot share airflow between zones.

 

Node and switch are shutting down based on its temperature, not the number of running fans.

If any fan in zone is failed, other fans in same zone will ramp up for proper cooling. If compute node's temperature is still increased, CPU will be throttled. If the temperature is still high, node will be shutting down due to over temperature condition. Switch module is also shutting down if it reaches the limit of over temperature.

 

Thank you,

Reply

Replies(2)
Answer
Options

82 Posts

04-23-2015

Japan

167 Signins

989 Page Views

  • Posts: 82
  • Registered: ‎04-23-2015
  • Location: Japan
  • Views: 989
  • Message 2 of 3

Re:Flex Chassis Fan Redundancy

2021-05-27, 0:44 AM

Hi Errrec,

 

Each zones are separated and cannot share airflow between zones.

 

Node and switch are shutting down based on its temperature, not the number of running fans.

If any fan in zone is failed, other fans in same zone will ramp up for proper cooling. If compute node's temperature is still increased, CPU will be throttled. If the temperature is still high, node will be shutting down due to over temperature condition. Switch module is also shutting down if it reaches the limit of over temperature.

 

Thank you,

1 person found this solution to be helpful.

This helped me too

Reply
Options

10 Posts

07-04-2020

India

19 Signins

150 Page Views

  • Posts: 10
  • Registered: ‎07-04-2020
  • Location: India
  • Views: 150
  • Message 3 of 3

Re:Flex Chassis Fan Redundancy

2021-05-27, 3:33 AM

Hi Yoshiros,

Thank you for your time & reply.

 

I understood, I couldn't find these details in the lenovo press/any product guide. It also means that Zone 3 & Zone 4 fan failures can make the IOMs unavailable.

Reply
Forum Home

Community Guidelines

Please review our Guidelines before posting.

Learn More

Check out current deals!

Go Shop
X

Save

X

Delete

X

No, I don’t want to share ideas Yes, I agree to these terms

Most Liked Authors

(Last 7 days)

View All