Lenovo D2 Enclosure SMM Email Alerts Configuration

2020-07-20, 7:09 AM

Hi,

 

Is there anyone who experience issue with email alerts notifications from Lenovo D2 Enclosure  SMM? From SMTP page when you click the Send Alert Tab we are able to receive the test mail from SMM. 

 

We have configure the SMTP settings from SMM and Global Alerting Enable in PEF page is checked including all the options in the PEF lists (all check).

 

The issue is when we unplug 1PSU as test, we are able to receive email alerts notification from SMM. But when we plug back 1PSU, theres no email notifications from SMM, is this normal?

 

Second, when we unplug 1 x SD530 node from the D2 Enclosure, we are not receiving any email alerts from SMM that one node is unplug but the from the event log it shows.

 

Thank you in advance for response.

 

Regards,

Jeff

Solved! See the solution
Reply
Options

67 Posts

04-12-2018

China

137 Signins

1534 Page Views

  • Posts: 67
  • Registered: ‎04-12-2018
  • Location: China
  • Views: 1534
  • Message 2 of 5

Re:Lenovo D2 Enclosure SMM Email Alerts Configuration

2020-07-21, 6:28 AM

Hi Jeff:

 

SMM only send critical level events alerts . After the PSU is unplugged, SMM will generate a Critical event, then send a email alert.  

It's informational level event for plugging the PSU back to the enclosure , So SMM won't send mail alert.

 

Also please check the SEL event severity level  when you unplug 1 x SD530 node from the D2 Enclosure,  SMM won't send mail alert if it's informational 

 

 

 

Reply
Options

53 Posts

07-13-2017

Saudi Arabia

108 Signins

1511 Page Views

  • Posts: 53
  • Registered: ‎07-13-2017
  • Location: Saudi Arabia
  • Views: 1511
  • Message 3 of 5

Re:Lenovo D2 Enclosure SMM Email Alerts Configuration

2020-07-21, 6:35 AM

Hi Rick,

 

Thanks for your response.

 

What about when one node has been unplug from the D2 chassis, it should send alert from SMM too or not?

 

Regards,

Jeff

 

 

Reply
Options

67 Posts

04-12-2018

China

137 Signins

1534 Page Views

  • Posts: 67
  • Registered: ‎04-12-2018
  • Location: China
  • Views: 1534
  • Message 4 of 5

Re:Lenovo D2 Enclosure SMM Email Alerts Configuration

2020-07-22, 7:09 AM

Hi Jeff:

 

I did a experiment on my lab machine. Here is SMM events generated by unplugging /plugging back the node.  The severity is normal hence SMM won't send alert mail. 

 

Event IDSeverityDate/Time ↓ Description 
0x21080142
Normal
2020-07-22 14:31:40 (UTC+0000)NODE3_PRESENT: Slot Or Connector sensor, Device Inserted / Device Present was asserted 
0x21880142
Normal
2020-07-22 14:31:29 (UTC+0000)NODE3_PRESENT: Slot Or Connector sensor, Device Inserted / Device Present was deasserted 

Please check the following guide for more SMM SEL details

https://thinksystem.lenovofiles.com/help/index.jsp?topic=%2F7X21%2Fsmm_error_messages.html&cp=3_0_11_0&anchor=smm_error_messages 

 

 

0 person found this solution to be helpful.

This helped me too

Reply
Options

53 Posts

07-13-2017

Saudi Arabia

108 Signins

1511 Page Views

  • Posts: 53
  • Registered: ‎07-13-2017
  • Location: Saudi Arabia
  • Views: 1511
  • Message 5 of 5

Re:Lenovo D2 Enclosure SMM Email Alerts Configuration

2020-07-22, 7:43 AM

Hi Rick,

 

Thanks for the response and clarifications.

 

Regards,

Jeff